A place to ask questions and add to probative and informative discussions associated with the various aspects of the field of fire investigation. -- FORUM RULES---BE CIVIL AND NO NAME CALLING, NO BELITTLING, NO BERATING, NO DENIGRATING others. Postings in violation of these rules can be removed or editted to remove the offending remarks at the discretion of the moderators and/or site administrator.
Re: Static & IBC's
Posted by:
cda (IP Logged)
Date: September 07, 2017 11:30AM
Is this what you are looking for::
5705.2.4 Class I, II and III Liquids
Class I liquids or, when heated to or above their flash points, Class II and Class III liquids, shall be transferred by one of the following methods:
1. From safety cans complying with UL 30.
2. Through an approved closed piping system.
3. From containers or tanks by an approved pump taking suction through an opening in the top of the container or tank.
4. For Class IB, IC, II and III liquids, from containers or tanks by gravity through an approved self-closing or automatic-closing valve where the container or tank and dispensing operations are provided with spill control and secondary containment in accordance with Section 5703.4. Class IA liquids shall not be dispensed by gravity from tanks.
5. Approved engineered liquid transfer systems.
Exception: Liquids in original shipping containers not exceeding a 5.3-gallon (20 L) capacity.