A place to ask questions and add to probative and informative discussions associated with the various aspects of the field of fire investigation. -- FORUM RULES---BE CIVIL AND NO NAME CALLING, NO BELITTLING, NO BERATING, NO DENIGRATING others. Postings in violation of these rules can be removed or editted to remove the offending remarks at the discretion of the moderators and/or site administrator. 
Re: Stove Top Extension
Posted by: dcarpenter ()
Date: March 10, 2014 02:14PM

As Pat put forth, the melting temperature of AL is much higher that the boiling temperature of water. Thus, as long as there is water in the pan, the temperature of the pan will not exceed the boiling point of the water. Therefore, the presence of the water in the pan is consistent with it being added to the pan after it had melted. This may be consistent with fire suppression activities.

You can test your hypothesis using some relatively simple plume correlations. You will need to know the thermal energy release rate of the electric coil, the diameter of the coil, along with the vertical height of interest. Since the AL pot on the coils will absorb thermal energy for some period of time, a "worst case" is the electric coil producing thermal energy with the pot.

The coils may have an thermal rating that is relatively small when compared to the heat release rate of hydrocarbon liquids with the same surface area. Although I have not done the calculation, I would think that the temperatures in the thermal plume a few feet in vertical height from the burner would not be close to the temperatures required for ignition of the wood cabinets.

The presence of "clean burns" at the front of the hood is consistent with direct flame impingement, which can provide a source of ignition for the wood cabinets about the hood. A flame height correlation is useful for testing such hypotheses.

Douglas J. Carpenter, MScFPE, CFEI, PE, FSFPE
Vice President & Principal Engineer
Combustion Science & Engineering, Inc.
8940 Old Annapolis Road, Suite L
Columbia, MD 21045
(410) 884-3266
(410) 884-3267 (fax)
www.csefire.com

Navigate: Previous MessageNext Message
Options: ReplyQuote


Subject Views Written By Posted
Stove Top Extension 2244 Jim Moon 03/10/2014 12:05PM
Re: Stove Top Extension 1122 J L Mazerat 03/10/2014 12:23PM
Re: Stove Top Extension 1109 John J. Lentini, CFEI 03/10/2014 12:32PM
Re: Stove Top Extension 1218 PMK140 03/10/2014 01:07PM
Re: Stove Top Extension 1204 dcarpenter 03/10/2014 02:14PM
Re: Stove Top Extension 1114 dcarpenter 03/10/2014 03:25PM
Re: Stove Top Extension 1112 jgmcfps 03/10/2014 06:19PM
Re: Stove Top Extension 1074 Jim Moon 03/14/2014 09:05AM


Sorry, only registered users may post in this forum.
This forum powered by Phorum.