Fire/Arson Investigations :  Fire/Arson Investigations The fastest message board... ever.
A place to ask questions and add to probative and informative discussions associated with the various aspects of the field of fire investigation. -- FORUM RULES---BE CIVIL AND NO NAME CALLING, NO BELITTLING, NO BERATING, NO DENIGRATING others. Postings in violation of these rules can be removed or editted to remove the offending remarks at the discretion of the moderators and/or site administrator. 
Re: Hu8midity and gasoline vapors
Posted by: dcarpenter (IP Logged)
Date: January 19, 2021 04:30PM

You may not find what your looking for in the available scientific literature with respect to empirical data. If you apply fundamentals, you will find the answer to your question.

The criteria that is relevant for ignition of gasoline vapors by the gas-fired water heater is a flammable concentration of gasoline vapors and air at the location of the source of ignition (inside the water heater enclosure). The criteria that the presence of any gasoline vapor at a vertical height of 18 inches is a necessary, but insufficient condition for the ignition of the gasoline vapors.

The "weight" of the gasoline vapors is not the relevant variable for consideration. It is the density of the gasoline vapors relative to the density of air that is relevant to whether gasoline vapors will be buoyant in air and will rise and opposed to falling. This ratio is refereed to as the Specific Gravity.

While humid air is less dense than dry air and will change the specific gravity, the effect of humidity is much less than other modes of mass transfer, such as diffusion and temperature effects. The forces associated with diffusion are strong enough to overcome the forces associated with gravity (buoyancy). The math suggests that the effect of humidity on the density of air is not significant at "room temperatures." This effect starts to change the specific gravity at temperatures well above "room temperature."

Gasoline is a multi-component mixture. All of the significant molecules of the individual components are "heavier" than air and will "fall" as opposed to rise. The way to change the specific gravity is to heat the gasoline vapors and reduce their density and specific gravity.

Since the characteristic time of diffusion is orders of magnitude greater than the characteristic time of forced convection, air movement is much more of a likely contributor for the flammable mixture at the source of ignition than the humidity in the air in most practical time frames. Given that the gas-fired water heater creates a buoyant flow internally and the combustion system requires air flow from outside, this is probably the determining factor for ignition. Again, the presence of a flammable concentration at the high of 18 inches outside the water heater is a necessary, but insufficient condition for ignition of gasoline vapors.

In summary, there is a change of density effect for changes in humidity of air, so one can formulate a hypothesis that this can cause a change in the vertical concentration gradient of gasoline vapors.However, if one tests this hypothesis using fundamentals of gas dynamics, basic chemistry, and thermodynamics, it would disprove this hypothesis (too small of an effect to be a driving force), but allow evidence to formulate other hypotheses.

Douglas J. Carpenter, MScFPE, CFEI, PE, FSFPE
Vice President & Principal Engineer
Combustion Science & Engineering, Inc.
8940 Old Annapolis Road, Suite L
Columbia, MD 21045
(410) 884-3266
(410) 884-3267 (fax)
www.csefire.com



Subject Views Written By Posted
  Hu8midity and gasoline vapors 715 J L Mazerat 01/16/2021 09:49AM
  Re: Hu8midity and gasoline vapors 450 dcarpenter 01/19/2021 09:43AM
  Re: Hu8midity and gasoline vapors 501 J L Mazerat 01/19/2021 12:03PM
  Re: Hu8midity and gasoline vapors 501 dcarpenter 01/19/2021 04:30PM
  Re: Hu8midity and gasoline vapors 442 J L Mazerat 01/20/2021 09:37AM
  Re: Hu8midity and gasoline vapors 370 Sir Gary 01/21/2021 05:07AM


Sorry, only registered users may post in this forum.
This forum powered by Phorum.