A place to ask questions and add to probative and informative discussions associated with the various aspects of the field of fire investigation. -- FORUM RULES---BE CIVIL AND NO NAME CALLING, NO BELITTLING, NO BERATING, NO DENIGRATING others. Postings in violation of these rules can be removed or editted to remove the offending remarks at the discretion of the moderators and/or site administrator. 
Re: Gould 30 Amp Cartridge Fuses
Posted by: Nick Markowitz (IP Logged)
Date: September 12, 2006 09:04PM

I have seen gould fuses that have failed but it was because they were misaplicated to the short circuit amperage the circuit calls for.
Class H fuse 30 amp which provides 10,000 amps short circuit protection would be acceptable for most household loads but heavy motor, transformer etc loads
would reguire a class R fuse which provides up to 100,000 short circuit amps protection. would need to know particulars to tell if fuses you had failed were the proper ones for the circuit they were being used in.