A place to ask questions and add to probative and informative discussions associated with the various aspects of the field of fire investigation. -- FORUM RULES---BE CIVIL AND NO NAME CALLING, NO BELITTLING, NO BERATING, NO DENIGRATING others. Postings in violation of these rules can be removed or editted to remove the offending remarks at the discretion of the moderators and/or site administrator.
Re: NFPA 54 procedure on gas run out
Posted by:
cda (IP Logged)
Date: November 20, 2008 10:03AM
from nfpa 54, not sure if it applies to what you ar looking for, and if propane maybe look at NFPA 58
have not heard of companies locking anything
5.9.6 Unauthorized Operation. Precautions shall be taken to prevent unauthorized operation of any shutoff valve that will make a pressure relieving valve or pressure limiting device inoperative. The following are acceptable methods for complying with this provision:
(1) Lock the valve in the open position. Instruct authorized personnel in the importance of leaving the shutoff valve open and of being present while the shutoff valve is closed so that it can be locked in the open position before leaving the premises.
(2) Install duplicate relief valves, each having adequate capacity to protect the system, and arrange the isolating valves or three-way valve so that only one safety device can be rendered inoperative at a time.
from nfpa 58:
(C) Fencing shall not be required where devices are provided that can be locked in place and prevent unauthorized operation of valves, equipment, and appurtenances.