A place to ask questions and add to probative and informative discussions associated with the various aspects of the field of fire investigation. -- FORUM RULES---BE CIVIL AND NO NAME CALLING, NO BELITTLING, NO BERATING, NO DENIGRATING others. Postings in violation of these rules can be removed or editted to remove the offending remarks at the discretion of the moderators and/or site administrator. 
Electrical Arc Surveys
Posted by: Mike Learmonth (IP Logged)
Date: November 15, 2006 10:52PM

Section 17.2.5 of NFPA 921-2004 added the subject of electrical arc surveys without providing much information on what it means and how to interpret it. Below I have written what I believe at first blush are the fundamentals of arc pattern analysis. Please provide any further insight you can give on this topic:

Fundamentals of arc pattern analysis:

1. Electrical arcing can only occur in an energized wire.
2. The severing of an electrical wire by melting either by arcing or from the heat of the fire, de-energizes that branch circuit from the location of the severing, to the load, so no further arcing can occur in that portion of the subject branch circuit.*
3. Because of that, multiple arcs resulting in the severing of the conductors in a particular branch circuit, must occur in the order from the location furthest away from the source of power to the location closest to the source of power.
4. Thus, multiple arcing locations on a single branch circuit with at least one arc severing location, may be used to define the sequence of the arcing incidents and thus, the direction the fire progressed in the area traversed by the particular branch circuit.
5. Electrical arcing (with or without complete conductor severing) may also trip the over-current protection device (or OCPD such as circuit breaker, fuse, etc.) rendering all of that particular circuit de-energized and thus no further arcing can occur anywhere on that branch circuit.
6. Tripping of the over-current protection device de-energizes every circuit power through that same OCPD.

* a rare exception that must be considered is circuits powered from two separate sources

Thanks for your input.

Michael A. Learmonth, B.A.Sc., M.B.A., M.Eng., J.D., LL.B., C.F.E.I., P.Eng.
Senior Associate, Giffin Koerth Forensic Engineering and Science
40 University Avenue, Suite 800
Toronto, Ontario, Canada M5J 1T1
Phone: 416-368-1700 ext. 225
Fax: 416-368-5576



Subject Views Written By Posted
  Electrical Arc Surveys 1604 Mike Learmonth 11/15/2006 10:52PM
  Re: Electrical Arc Surveys 1032 cda 11/16/2006 08:52AM
  Re: Electrical Arc Surveys 1146 ForensicEEnMD 11/16/2006 12:55PM
  Re: Electrical Arc Surveys 1031 Mike Learmonth 11/16/2006 08:04PM
  Re: Electrical Arc Surveys 1112 Thomas Sing 11/16/2006 10:31PM
  Re: Electrical Arc Surveys 1000 Mike Learmonth 11/16/2006 11:01PM
  Re: Electrical Arc Surveys 1358 ForensicEEnMD 11/17/2006 10:46AM
  Re: Electrical Arc Surveys 979 G Van Doren 11/16/2006 10:26PM


Sorry, only registered users may post in this forum.
This forum powered by Phorum.