A place to ask questions and add to probative and informative discussions associated with the various aspects of the field of fire investigation. -- FORUM RULES---BE CIVIL AND NO NAME CALLING, NO BELITTLING, NO BERATING, NO DENIGRATING others. Postings in violation of these rules can be removed or editted to remove the offending remarks at the discretion of the moderators and/or site administrator. 
Re: Over-Lamping Condition
Posted by: rwkovarsky (IP Logged)
Date: February 11, 2007 03:24PM

Had a fire where a 250 watt bubl was placed into a recessed fixture in a kitchen soffitt. The fixture's markings indicated it was rated for 100 watts or less. The overlamping caused an overheating of the fixture housing and ignited adjacent framing materials. The fixture and bulb were still intact at the time of my examination.

Overlamping should not cause any overheating issues on the branch circuit wiring associated with the fixture. A 100 watt bulb draws just under 1 amp, while a 250 watt bulb is just over 2 amps. This is well within the current handling capacity of all branch cirucit wiring and of almost all extension cords. Therefore, the overlamping should have no adverse effect on the cable based strictly on the current draw.

Hope this helps!

Rich Kovarksy, P.E., CFEI
Pyro-Technical Investigations
www.ptiforensic.com



Subject Views Written By Posted
  Over-Lamping Condition 1525 RKERSEY 02/11/2007 01:05PM
  Re: Over-Lamping Condition 936 rwkovarsky 02/11/2007 03:24PM
  Re: Over-Lamping Condition 998 Nick Markowitz 02/11/2007 10:41PM
  Re: Over-Lamping Condition 906 Ted Pagels 02/12/2007 09:26AM


Sorry, only registered users may post in this forum.
This forum powered by Phorum.