A place to ask questions and add to probative and informative discussions associated with the various aspects of the field of fire investigation. -- FORUM RULES---BE CIVIL AND NO NAME CALLING, NO BELITTLING, NO BERATING, NO DENIGRATING others. Postings in violation of these rules can be removed or editted to remove the offending remarks at the discretion of the moderators and/or site administrator. 
Re: Baled hay fires
Posted by: dcarpenter (IP Logged)
Date: October 26, 2018 10:48AM

I seem to be unclear as to what you are asking for. It seems you are looking for the ability to characterize a time interval. Can you be more clear?

These fires are the result of self-heating to thermal runaway. The most significant variables are the size of the pile and the exposure temperature. They are coupled in this case, so there is no single temperature or pile sizes. Only a critical pile size for a specified exposure temperature and a critical temperature for a specified pile size.

There is a theoretical and quantitative means to estimate the time to thermal runaway if the FK parameters are known. There is some data on this in P C Bowes. So for a given pile size and temperature, one can estimate the time to thermal runaway, at least in the context of an order of magnitude (minutes, hours, days, weeks, months). This reference was published in your "neck of the woods" by BRE and the Crown. See the SFPE Handbook of Fire Protection Engineering for the theory of the FK methodology. The problem is that the estimated time to thermal runaway can only be assessed at the point when the FK parameters predict first thermal runaway and not if theses parameters significantly exceed this critical point. Thus, useful in some cases, but not for all values of the pile size and temperatures.

See:

Bowes, P. C., "Self-heating: Evaluating and Controlling the Hazards," Building Research Establishment, Her Majesty's Stationary Office, London, 1984.

Babrauskas, V., Ignition Handbook, pp. 845 to 847 ...

Douglas J. Carpenter, MScFPE, CFEI, PE, FSFPE
Vice President & Principal Engineer
Combustion Science & Engineering, Inc.
8940 Old Annapolis Road, Suite L
Columbia, MD 21045
(410) 884-3266
(410) 884-3267 (fax)
www.csefire.com



Subject Views Written By Posted
  Baled hay fires 1136 Sir Gary 10/26/2018 06:37AM
  Re: Baled hay fires 696 dcarpenter 10/26/2018 10:48AM
  Re: Baled hay fires 661 Sir Gary 10/30/2018 06:51AM
  Re: Baled hay fires 651 Sir Gary 10/30/2018 06:56AM
  Re: Baled hay fires 664 dcarpenter 11/01/2018 11:49AM
  Re: Baled hay fires 614 dcarpenter 11/01/2018 11:51AM
  Re: Baled hay fires 618 Sir Gary 11/02/2018 08:07AM