Fire/Arson Investigations :  Fire/Arson Investigations The fastest message board... ever.
A place to ask questions and add to probative and informative discussions associated with the various aspects of the field of fire investigation. -- FORUM RULES---BE CIVIL AND NO NAME CALLING, NO BELITTLING, NO BERATING, NO DENIGRATING others. Postings in violation of these rules can be removed or editted to remove the offending remarks at the discretion of the moderators and/or site administrator. 
Re: Second floor window apartment building escape
Posted by: BaFire2762 (IP Logged)
Date: July 13, 2022 07:11PM

My state uses NFPA 101 (2018 Ed.), for 1-2 families it is 20 feet. Existing apartment buildings have to comply with the requirements of this section as well according to that chapter.

31.2.1.2 Means of escape within the dwelling unit shall comply with the provisions of Section 24.2 for one- and two-family dwellings.

24.2.2.3.3* It shall be an outside window or door operable from the inside without the use of tools, keys, or special effort
2 and shall provide a clear opening of not less than 5.7 ft
(0.53 m2). The width shall be not less than 20 in. (510 mm), and the height shall be not less than 24 in. (610 mm). The bottom of the opening shall be not more than 44 in. (1120 mm) above the floor. Such means of escape shall be acceptable where one of the following criteria is met:

(1) The window shall be within 20 ft (6100 mm) of the finished ground level.



Subject Views Written By Posted
  Second floor window apartment building escape 374 J L Mazerat 07/13/2022 04:00PM
  Re: Second floor window apartment building escape 256 BaFire2762 07/13/2022 07:11PM
  Re: Second floor window apartment building escape 231 J L Mazerat 07/15/2022 08:11AM
  Re: Second floor window apartment building escape 245 DG29 07/18/2022 05:22PM
  Re: Second floor window apartment building escape 215 J L Mazerat 07/18/2022 07:21PM


Sorry, only registered users may post in this forum.
This forum powered by Phorum.