A place to ask questions and add to probative and informative discussions associated with the various aspects of the field of fire investigation. -- FORUM RULES---BE CIVIL AND NO NAME CALLING, NO BELITTLING, NO BERATING, NO DENIGRATING others. Postings in violation of these rules can be removed or editted to remove the offending remarks at the discretion of the moderators and/or site administrator. 
Re: Test burn question for Corbett, Hicks, Kennedy & Hopkins
Posted by: greggorbett (IP Logged)
Date: August 29, 2006 06:41PM

As this was the first set of replicate burns, all of the procedural issues were not yet refined. The biggest procedural issue is the opening and closing of vents (i.e. doors and windows). The first test (the one taking longer to achieve flashover) initially had the outside doors closed. As we were watching the fire progress, it was determined that the fire was vitiating. Therefore, the outside door was opened slightly, which allowed the fire to grow again and transition through flashover. We planned accordingly for the second test and allowed the outside door to be left slightly open.

Since the first set of tests, we have implemented a procedure for controlling the ventilation opening by utilizing pieces of wood to hold open the doors at the same angle. A testament for this “now-refined” procedure is that the remaining set of replicate tests reveals almost identical fire growth and time/temperature curves. As I am sure you are aware, the Advanced Fire Pattern Research Project (AFPRP) co-sponsored all test burns and focused its research interests on fire pattern development and reproducibility. Therefore, it should be noted that the fire pattern development in both compartments were not affected by the difference in the time to flashover, which is a critical part of our research.

Hopefully, this answers your question regarding flashover time being variable. If you have the ISFI 2006 paper (part of the ISFI proceedings) you could see the similarities of the remaining 4 test burns. If you do not have a copy of the proceedings, you can obtain a copy through www.nafi.org.

If you have any further questions or concerns please feel free to contact any of us. Thanks for your patience in waiting for this reply...as Patrick had mentioned I was sick, but I am feeling better now.

Best regards,

Gregory E. Gorbett, CFEI, CFPS, MIFireE, IAAI-CFI
Patrick M. Kennedy, CFEI, CFPS, MIFireE
Ron Hopkins, CFEI, CFPS



Subject Views Written By Posted
  Test burn question for Corbett, Hicks, Kennedy & Hopkins 1887 jmorse 08/23/2006 08:20PM
  Re: Test burn question for Corbett, Hicks, Kennedy & Hopkins 1153 PMK140 08/26/2006 09:28PM
  Re: Test burn question for Corbett, Hicks, Kennedy & Hopkins 994 jmorse 08/28/2006 01:29AM
  Re: THE ADVANCED FIRE PATTERN ANALYSIS RESEARCH PROJECT 1138 PMK140 08/31/2006 09:11AM
  Re: Test burn question for Corbett, Hicks, Kennedy & Hopkins 1098 greggorbett 08/29/2006 06:41PM
  Re: Test burn question for Corbett, Hicks, Kennedy & Hopkins 1034 John J. Lentini, CFEI 08/30/2006 05:22PM
  Re: Test burn question for Corbett, Hicks, Kennedy & Hopkins 965 greggorbett 08/31/2006 08:05AM
  Re: Test burn question for Corbett, Hicks, Kennedy & Hopkins 953 Ted Pagels 08/30/2006 09:10PM
  Re: Test burn question for Corbett, Hicks, Kennedy & Hopkins 1028 PMK140 08/31/2006 07:41AM
  Re: Test burn question for Corbett, Hicks, Kennedy & Hopkins 1071 greggorbett 08/31/2006 07:55AM
  Re: Test burn question for Corbett, Hicks, Kennedy & Hopkins 982 Ted Pagels 08/31/2006 09:26PM
  Re: Test burn question for Corbett, Hicks, Kennedy & Hopkins 964 jmorse 09/01/2006 05:49PM