A place to ask questions and add to probative and informative discussions associated with the various aspects of the field of fire investigation. -- FORUM RULES---BE CIVIL AND NO NAME CALLING, NO BELITTLING, NO BERATING, NO DENIGRATING others. Postings in violation of these rules can be removed or editted to remove the offending remarks at the discretion of the moderators and/or site administrator. 
Re: Minimum Ignition Energy (mJ) of gases
Posted by: dcarpenter (IP Logged)
Date: January 02, 2018 03:35PM

I can only assume by your questions that you missed the point of my previous posting. However, I will engage your inquiry in the context of promoting education and the reliable application of fundamental knowledge.

The minimum ignition energy for Methane is from the classic reference:

Zebetakis, M.G. (1965), "Flammability Characteristics of Combustible Gases and Vapours," U.S. Bureau of Mines, Bulletin 627.

You will find a reproduction of the ignitability curve and limits of flammability for methane/air mixtures at atmospheric pressure and 26 degrees Celsius. This can be found on Page 87 of Dougal Drysdale's "An Introduction to Fire Dynamics," third edition.

I sense you are looking for the most accurate value for the MIE. As you may know, the concentration plays a role in this value and the MIE is found at the rich side of the Stoichiometric fuel/air ratio. The flammability limits widen with increasing temperature, so the most accurate value will be in the context of the associated temperature and pressure.

The values reported by Zebetakis were done with a specific apparatus developed by the U.S. Bureau of Mines. I have not assessed any differences in this work and the current ASTM standard. Again, in this application context, why is this significant beyond trying exploit inaccuracies in expert testimony that may not have any significance to the outcome of the analysis of the ignition of flammable vapors?

J L Mazerat Wrote:
-------------------------------------------------------
> Doug:
>
> I am not doubting you on your information. I
> assume the value you cite is from a ASTM E-582
> test. You cite the minimum ignition energy for
> methane as being .29 mJ. I have some questions
> based on the information contained in the
> standard. What was the test that produced that
> value? How many times were the test run? Were the
> results exactly the same each time. What was the
> concentration used in the test? Was there any
> variance in the concentration? If I were to have
> altered the concentration by .01% how much would
> that have changed the value, if any?

Douglas J. Carpenter, MScFPE, CFEI, PE, FSFPE
Vice President & Principal Engineer
Combustion Science & Engineering, Inc.
8940 Old Annapolis Road, Suite L
Columbia, MD 21045
(410) 884-3266
(410) 884-3267 (fax)
www.csefire.com



Subject Views Written By Posted
  Minimum Ignition Energy (mJ) of gases 1556 J L Mazerat 12/29/2017 09:47AM
  Re: Minimum Ignition Energy (mJ) of gases 839 Mark Goodson 12/29/2017 10:47AM
  Re: Minimum Ignition Energy (mJ) of gases 839 J L Mazerat 12/29/2017 03:09PM
  Re: Minimum Ignition Energy (mJ) of gases 804 rdzimm 12/30/2017 01:25PM
  Re: Minimum Ignition Energy (mJ) of gases 832 Fire 12/30/2017 01:32PM
  Re: Minimum Ignition Energy (mJ) of gases 805 Sir Gary 12/31/2017 12:31AM
  Re: Minimum Ignition Energy (mJ) of gases 840 J L Mazerat 12/30/2017 08:06PM
  Re: Minimum Ignition Energy (mJ) of gases 842 John Lentini 12/31/2017 05:13PM
  Re: Minimum Ignition Energy (mJ) of gases 819 J L Mazerat 12/31/2017 08:19PM
  Re: Minimum Ignition Energy (mJ) of gases 778 Chris Bloom, CJBFireConsultant 01/02/2018 03:06AM
  Re: Minimum Ignition Energy (mJ) of gases 760 J L Mazerat 01/02/2018 10:13AM
  Re: Minimum Ignition Energy (mJ) of gases 768 dcarpenter 01/02/2018 11:49AM
  Re: Minimum Ignition Energy (mJ) of gases 802 J L Mazerat 01/02/2018 12:31PM
  Re: Minimum Ignition Energy (mJ) of gases 859 dcarpenter 01/02/2018 01:44PM
  Re: Minimum Ignition Energy (mJ) of gases 790 J L Mazerat 01/02/2018 03:20PM
  Re: Minimum Ignition Energy (mJ) of gases 795 dcarpenter 01/02/2018 03:54PM
  Re: Minimum Ignition Energy (mJ) of gases 767 dcarpenter 01/02/2018 03:58PM
  Re: Minimum Ignition Energy (mJ) of gases 755 J L Mazerat 01/02/2018 07:13PM
  Re: Minimum Ignition Energy (mJ) of gases 796 J L Mazerat 01/02/2018 07:12PM
  Re: Minimum Ignition Energy (mJ) of gases 901 dcarpenter 01/02/2018 01:58PM
  Re: Minimum Ignition Energy (mJ) of gases 770 J L Mazerat 01/02/2018 02:31PM
  Re: Minimum Ignition Energy (mJ) of gases 769 dcarpenter 01/02/2018 03:35PM
  Re: Minimum Ignition Energy (mJ) of gases 777 dcarpenter 01/02/2018 05:25PM
  Re: Minimum Ignition Energy (mJ) of gases 750 J L Mazerat 01/02/2018 07:27PM
  Re: Minimum Ignition Energy (mJ) of gases 787 J L Mazerat 01/02/2018 07:18PM