A place to ask questions and add to probative and informative discussions associated with the various aspects of the field of fire investigation. -- FORUM RULES---BE CIVIL AND NO NAME CALLING, NO BELITTLING, NO BERATING, NO DENIGRATING others. Postings in violation of these rules can be removed or editted to remove the offending remarks at the discretion of the moderators and/or site administrator.
Re: Ignition temperature of wood
Posted by:
dcarpenter (IP Logged)
Date: September 29, 2020 01:41PM
The "ignition temperature" of wood is reported for piloted ignition of a wood surface being exposed to a thermal radiant flux. This is not the same as the ignition temperature due to self-heating, which is not a single value, but must be reported with respect to a critical dimension or characteristic length. Wood will ignite at "room temperature, if the critical length is achieved. The smaller the "pile size" the higher the critical temperature. The opposite is also true.
"All the results were that low temperature long-term exposure can cause ignition of wood below it reported ignition temperature." This is currently true for a range of temperatures on the order of 150 degrees C depending on the critical length for the material. This is not currently a reliable determination for temperatures on the order of 77 to 100 degrees C for dimensional lumber.
Douglas J. Carpenter, MScFPE, CFEI, PE, FSFPE
Vice President & Principal Engineer
Combustion Science & Engineering, Inc.
8940 Old Annapolis Road, Suite L
Columbia, MD 21045
(410) 884-3266
(410) 884-3267 (fax)
www.csefire.com